Re: apcupsd sc420i line voltage
On 07.12.2022 19:47, Vukovics Mihály
wrote:
Hello
Community,
I am strugling with APC SmartUPS SC420I and apcupsd.
The UPS is connected via usb-to serial adapter and 940-0024E
cable.
The UPS is recognized as "Back-UPS Pro 280" instead of SC420I and
the line voltage is displayed as 120V instead of the real 230V.
UPSTYPE apcsmart
DEVICE /dev/ttyUSB0
Has any of you experienced like this and know how to fix at least
the line voltage value?
Maybe it would be better to try "nut-server" which could have a
better apcsmart driver implementation?
I have APC SmartUPS SC1500I with similar setup, USB-to-COM adapter
and self-made APC UPS Smart cable and it is working fine with
nut-server, both monitoring and control.
Another thing to check could be an usb-to-serial adapter. I've seen
some cheap low-quality adapters which were created with counterfeit
ICs.
--
With kindest regards, Alexander.
⢀⣴⠾⠻⢶⣦⠀