Re: APC UPS CS500 won't switch on again



On Sat, 26 Feb 2005 16:20:08 +0100, Matthijs <vanaalten@hotmail.com>
wrote:

> On Sat, 26 Feb 2005 13:00:17 +0100, Alexei Chetroi
> <alexei.chetroi@debian.uniflux-line.net> wrote:
> 
> > Disconnect usb cable and leave ups on battery until it switches off by
> > himself. Connect it to the power again and chech if it will power on
> > load. So you can tell wether ups doesn't bring on load or it told to do
> > so.
> 
> Sounds like a good test - I'll see if I can perform this. Disadvantage
> is that the server will not shutdown in a proper manner, but for one
> time the chance of damage is acceptable.

I've done another test instead: connected the UPS to a windows-XP
machine, installed the manufacturer's software and tested it. It works
exactly as I would expect: after shutting down the PC, some seconds
later the OnLine/OverLoad lights on the UPS start flashing and the UPS
shuts down - or so it appears.
But now, when I reconnect the mains cable, the UPS wakes up from
standby and then wakes up the PC.

So, conclusions:
- UPS is not malfunctioning;
- UPS USB cable is OK;
- probably apcupsd on the Debian box is signalling a full shut-down to
the UPS instead of a standby command.

Anyone out there with an APC CS-500 (or similar) who recognizes the
problem and is willing to share his/her setup?
-- 
Matthijs
vanaalten@hotmail.com