Re: apcupsd - system shut down on self test



Darac Marjal wrote:

> Run "apcaccess" and look at the following values:
> TIMELEFT - This is how long the UPS believes it is able to run the
> current load for, given the state of the batteries.
> MINTIMEL - This is, essentially, the amount of time the administrator
> believes is necessary to shut the load (i.e. Computer) down.
> 
> If TIMELEFT drops below MINTIMEL while the UPS is on batteries, then APC
> will begin shutting down the computer. Reasons it may do that after two
> seconds include failing batteries or simply that the run time is too
> short (i.e. your UPS does not have enough battery capacity to run the
> devices you have connected to it).

Hi, thank you.
Should I switch off the power supply of the UPS to see the values when on
battery

Now it has followin

# apcaccess  | grep TIMELEFT
TIMELEFT : 42.8 Minutes

# apcaccess  | grep MINTIMEL
MINTIMEL : 3 Minutes

Thanks again!