Re: APC (American Power Conversion) APC BACK-UPS RS 800VA
Hi Antti
I forgot to mention that for my two amd64 dual opterons set the transformer is
600W. Would the 540W of APC BACK-UPS RS 800VA be enough? The 1000W model is
priced 470 euros in Italy.
thanks again
francesco pietra
On Saturday 13 May 2006 18:19, Antti Pyykko wrote:
> On Sat, 13 May 2006, Francesco Pietra wrote:
> > I have been offered in my country (Italy) APC (American Power Conversion)
> > APC BACK-UPS RS 800VA
>
> [ snip ]
>
> > Has anyone experience with this (or other equipment to the same purpose)
> > for the type on installation of my project?
>
> I am using that very UPS with my system. I run apcups with it and it
> works very well. I suggest you forget powerchute and use apcupsd.
>
>
> [113320] [19:16] pyksy@hanuri.dap ~ % apcaccess status
> APC : 001,040,0980
> DATE : Sat May 13 19:16:13 EEST 2006
> HOSTNAME : hanuri.dap
> RELEASE : 3.12.1
> VERSION : 3.12.1 (06 January 2006) debian
> UPSNAME : APC
> CABLE : USB Cable
> MODEL : Back-UPS BR 800
> UPSMODE : Stand Alone
> STARTTIME: Tue Mar 14 03:46:34 EET 2006
> STATUS : ONLINE
> LINEV : 228.0 Volts
> LOADPCT : 26.0 Percent Load Capacity
> BCHARGE : 100.0 Percent
> TIMELEFT : 31.5 Minutes
> MBATTCHG : 5 Percent
> MINTIMEL : 3 Minutes
> MAXTIME : 0 Seconds
> OUTPUTV : 230.0 Volts
> DWAKE : 000 Seconds
> DSHUTD : 000 Seconds
> LOTRANS : 194.0 Volts
> HITRANS : 264.0 Volts
> RETPCT : 000.0 Percent
> ITEMP : 29.2 C Internal
> ALARMDEL : Always
> BATTV : 27.8 Volts
> LINEFREQ : 50.0 Hz
> LASTXFER : Low line voltage
> NUMXFERS : 0
> TONBATT : 0 seconds
> CUMONBATT: 0 seconds
> XOFFBATT : N/A
> SELFTEST : NO
> STATFLAG : 0x07000008 Status Flag
> SERIALNO : QB0420246146
> BATTDATE : 2001-09-25
> NOMBATTV : 24.0
> FIRMWARE : .o2 .I USB FW:o2
> APCMODEL : Back-UPS BR 800
> END APC : Sat May 13 19:16:22 EEST 2006
>
> --